kentaylor04
Member
have a 6 gang meter socket total calculated demand on 6 apt.s 238 amps. feeder sized at 500mcm copper. this sound right?
Jim how do we know that, there is no 250 amp OCP?Originally posted by jtester:
Remember, you can probably use Table 310.15(B)(6) to size service conductors and feeders if you choose to reduce your service size. Per that table you could use 4/0 copper.
Jim T
But I'm still not sure if that answers your question. I think the reason this reduction in size is allowed is because the POCO will size the service conductors even smaller.Section 230.42 requires service conductors to be of sufficient size to carry the load calculated in accordance with article 220.
That is the heart of my question, a conductor is a conductor in a house or a office building.Originally posted by jtester:
I believe that Table 310.15(B)(6) increases the permissible capacity of the wire determined under certain circumstances.
I completely agree, hence my proposal to eliminate standard and optional calculations for dwellings, replacing them with a simplified minimum calculation that is more accurate and more comparable to actual loads experienced in typical dwellings.Originally posted by iwire:
IMO a better way to handle this issue would be revisions to Article 220 that bring the calculated load closer to the actual load. Then get ride of Table 310.15(B)(6) altogether.
Thanks all, Bob
Originally posted by jtester:
The more I type, the more convoluted it sounds,