I have an unmetered service switch that needs Arc Energy Reduction device...
240.67(B) requires fuses to trip at 0.07 seconds or less at the available arcing current. The Arc Energy Reduction methods are these according to the code:
(1) Differential relaying
(2) Energy-reducing maintenance switching with local status indicator
(3) Energy-reducing active arc-flash mitigation system
(4) Current-limiting, electronically actuated fuses
(5) An approved equivalent means
all of these methods require power to the Arc Energy Reduction device. So if I have an unmetered service switch can I use the unmetered conductors of the service switch to power it? Would that be even legal since it's sort of like stealing energy? I see this one product that does this but can it be used if the service switch is unmetered? See this link to the product: https://boltswitch.com/pdf/Boltswitch_AFR_AFGFR_Flyer.pdf
240.67(B) requires fuses to trip at 0.07 seconds or less at the available arcing current. The Arc Energy Reduction methods are these according to the code:
(1) Differential relaying
(2) Energy-reducing maintenance switching with local status indicator
(3) Energy-reducing active arc-flash mitigation system
(4) Current-limiting, electronically actuated fuses
(5) An approved equivalent means
all of these methods require power to the Arc Energy Reduction device. So if I have an unmetered service switch can I use the unmetered conductors of the service switch to power it? Would that be even legal since it's sort of like stealing energy? I see this one product that does this but can it be used if the service switch is unmetered? See this link to the product: https://boltswitch.com/pdf/Boltswitch_AFR_AFGFR_Flyer.pdf