We have a piece of energy metering installed at an industrial client facility. The readings from the meter look to be normal except whenever the facility test the back-up generator at the facility, during which we see unusual readings from the metering, namely that the real and reactive power begin to oscillate, with a cycle taking between 13 and 19 seconds to complete.
We are not sure what the exact cause of this issue is. We have suspicions that the cause could be that the voltage reference is on the utility side of the transfer switch between the utility and generator system, and the Current transformers are located on the load side of the transfer switch; but do not have documentation of the installation to be certain about this.
Are there any suggestions as to what is going on with the system, or alternative potential causes?
Below are pictures of charts for 100ms data collected during one of these events. (Cannot figure out how to embed images, so added google drive Links. If I get feedback on how to embed images I will update accordingly).
Overview: https://drive.google.com/file/d/1G1eMwWstdLQL9uGHQDJnEu6TEtJ37W9g/view?usp=sharing
Frequency (Slight increase during event): https://drive.google.com/file/d/1-RvD-Cz0wmxTbIxtS_-4ryWzij3Z0vzE/view?usp=sharing
LL/LN Voltage (Slight decrease during event): https://drive.google.com/file/d/1YTVe6LLINLgaDhS75guO4qoc0yrUlEWQ/view?usp=sharing
Current: https://drive.google.com/file/d/1JBKlJ6740ZeKsLoQO7hq_YvzBrnqbLcC/view?usp=sharing
Apparent Power: https://drive.google.com/file/d/19ZTHE1XaUa5AQjeeMkF9jlhaKyLzUsRg/view?usp=sharing
Demand: https://drive.google.com/file/d/1MmWqh4p4VJEMoWHZvCTLu7ukz3z_CKav/view?usp=sharing
Power Factor: https://drive.google.com/file/d/1P-jr-wSTKzjaY3Bw7e_pl34p-59ukHPN/view?usp=sharing
We are not sure what the exact cause of this issue is. We have suspicions that the cause could be that the voltage reference is on the utility side of the transfer switch between the utility and generator system, and the Current transformers are located on the load side of the transfer switch; but do not have documentation of the installation to be certain about this.
Are there any suggestions as to what is going on with the system, or alternative potential causes?
Below are pictures of charts for 100ms data collected during one of these events. (Cannot figure out how to embed images, so added google drive Links. If I get feedback on how to embed images I will update accordingly).
Overview: https://drive.google.com/file/d/1G1eMwWstdLQL9uGHQDJnEu6TEtJ37W9g/view?usp=sharing
Frequency (Slight increase during event): https://drive.google.com/file/d/1-RvD-Cz0wmxTbIxtS_-4ryWzij3Z0vzE/view?usp=sharing
LL/LN Voltage (Slight decrease during event): https://drive.google.com/file/d/1YTVe6LLINLgaDhS75guO4qoc0yrUlEWQ/view?usp=sharing
Current: https://drive.google.com/file/d/1JBKlJ6740ZeKsLoQO7hq_YvzBrnqbLcC/view?usp=sharing
Apparent Power: https://drive.google.com/file/d/19ZTHE1XaUa5AQjeeMkF9jlhaKyLzUsRg/view?usp=sharing
Demand: https://drive.google.com/file/d/1MmWqh4p4VJEMoWHZvCTLu7ukz3z_CKav/view?usp=sharing
Power Factor: https://drive.google.com/file/d/1P-jr-wSTKzjaY3Bw7e_pl34p-59ukHPN/view?usp=sharing