On my advice, friends are deploying a The Energy Detective metering system. This will put CT's and other parts inside panelboards.
TED sent a certification document "TEST REPORT IEC 61010-1 Safety requirements for electrical equipment for measurement, control, and laboratory use" stating "The products covered by this report are Energy Monitoring Systems consisting of a Measuring and Transmitting Unit (MTU) intended to be installed inside a service or distribution panel along with Current Transformers for up to 3 phases and breaker wiring, and a Gateway (GW) that plugs into an outlet and communicates with the MTU over a Power Line Carrier (PLC)." (Full document available on request; it's a 6 MB pdf.)
But in one case, the CT's will be in a fused disconnect upstream of the panel. The EC is nervous the AHJ won't allow the CT's in that disconnect & a conduit from it for the metering cable. Is a disconnect a "service or distribution panel" in this case?
TED sent a certification document "TEST REPORT IEC 61010-1 Safety requirements for electrical equipment for measurement, control, and laboratory use" stating "The products covered by this report are Energy Monitoring Systems consisting of a Measuring and Transmitting Unit (MTU) intended to be installed inside a service or distribution panel along with Current Transformers for up to 3 phases and breaker wiring, and a Gateway (GW) that plugs into an outlet and communicates with the MTU over a Power Line Carrier (PLC)." (Full document available on request; it's a 6 MB pdf.)
But in one case, the CT's will be in a fused disconnect upstream of the panel. The EC is nervous the AHJ won't allow the CT's in that disconnect & a conduit from it for the metering cable. Is a disconnect a "service or distribution panel" in this case?