gooseloony
Member
Does the NEC allow or disallow a suite in say a commercial strip mall shopping center to have two seperate panelboards being fed from two seperate service meters (which are installed in one multi-meter MSB)? Thanks in advance.
This has nothing to do with the NEC.Originally posted by gooseloony:
Our local utility planner says "Absolutely NOT will they set a second meter for the same tenant space"--
A lot of "ifs" in that but in practice the answer is no.304. Number of Services
A. Per Building: One alternating current service will normally be installed to a building. Requests for additional services will be reviewed on an individual basis. Even if approved by the inspection authority having jurisdiction, it will be installed at the option of the Company. A construction advance may be required.
B. Per Premises:
If a Customer desires more than one service in order to separately meter another building on the same premises, and if this building could otherwise be supplied through the one meter and if the Company allows such additional service, the Customer shall pay the entire cost of installing the additional service.
It depends on the rules and law where you are located. Indiana law prohibits the reselling of electricity unless you are an electric utility. However, you are permitted to master meter and use sub-meters to split the electric bill among the users.Are you allowed to install your own meter and resell the electricity to the tenant?
It makes no difference, the power company can refuse to provide a second meter for the same tenant.Originally posted by mc5w:
If the metering center has a single service circuit breaker then the meter is in a FEEDER.
What the heck are you talking about?Originally posted by mc5w:
In fact, a 400 amp 120Y208 volt line is essentially two 200 amp line joined together at both ends. Because of neutral heating due to electric discharge lighting, computers, and so forth you would need 250 KCM copper for each phase conductor plus 1 or 2 250 KCM for the neutral for a 200 amp line. You would need 2 conduits for 400 amps plus the hassle of routing the conduits so that they are each of the same exact length.