When obtaining short circuit current for a bucket in a 600V class MCC. Given the following: 3ph 480VAC 30A adjustable trip CB, size 2 NEMA rated, contactor w/OL, and a 15HP motor.
I understand, per the 70E using the IEEE Calculation method, the max current is obtained at the Instantaneous Trip of the short circuit protection point ( the CB ). The debate at work is to somehow use the FLA of the motor. I might even understand if the value used was the locked rotor current. Yet this also has its issues as normal CB selection allows for the selection of CB's which can avoid tripping during startup.
I believe using motor related data will give a calculated value for incident energy much lower than actual. I understand there are many methods for calculating incident energy, I'm not an EE and don't know all of them.
1. Is there a method which uses FLA of the motor as the data for the calculation?
2. If this method is accurate, does it give a liberal lower incident energy?
I understand, per the 70E using the IEEE Calculation method, the max current is obtained at the Instantaneous Trip of the short circuit protection point ( the CB ). The debate at work is to somehow use the FLA of the motor. I might even understand if the value used was the locked rotor current. Yet this also has its issues as normal CB selection allows for the selection of CB's which can avoid tripping during startup.
I believe using motor related data will give a calculated value for incident energy much lower than actual. I understand there are many methods for calculating incident energy, I'm not an EE and don't know all of them.
1. Is there a method which uses FLA of the motor as the data for the calculation?
2. If this method is accurate, does it give a liberal lower incident energy?