electricalist
Senior Member
- Location
- dallas tx
For branch circuit's like offices 4 plugs 2 3 lamp 2x4 lights and everything is 120 v. Ivebeen reading about derating and Iim trying to see if im learning or getting confused. 3 hots a b c phase & 1 neutral are ideal for plugs . If i got it right this is 3 current carying conductors? The neutral being balanced. . If Iit were 1 hot and 1 neutral it is unbalanced. For derating this is 2 ccc. What if its 2 hots 1 neutral a & b phase. If a full boat is a theoretically better combination. I think for derating. 3 full boats in a conduit will keep me code compliant for a 20 amp circuit #12 wire and 20 amp breaker. Next its the linear and non. Linear being things with controlled voltage at the equipment electronic ballast vfd. Non would be outlets. Non can be a problem do to 3 rd harmonic adding to heat problems on the neutral. Should not mix them . Keep plus and lights seperate.