Here's another question, I think I got it right.
the 20 I 240 volt copper conductor branch ckt. installed to control metal pole lights at a traffic intersection shall be permitted to contain:
A) 2#8 awg thwn & 1 # 8 thwn equipment ground
B) 2#10 awg thwn & 1 #12 awg thwn equipment ground
C) 2#10 awg thwn, when the polebase rebar cage provides the ground means.
D) 2#12 awg thwn, when a ground rod is driven at the pole base.
Answer: B . 20 I ckt I went with the #10
because the 80% Still not shure and didn't see in 250 anything else?
the 20 I 240 volt copper conductor branch ckt. installed to control metal pole lights at a traffic intersection shall be permitted to contain:
A) 2#8 awg thwn & 1 # 8 thwn equipment ground
B) 2#10 awg thwn & 1 #12 awg thwn equipment ground
C) 2#10 awg thwn, when the polebase rebar cage provides the ground means.
D) 2#12 awg thwn, when a ground rod is driven at the pole base.
Answer: B . 20 I ckt I went with the #10
because the 80% Still not shure and didn't see in 250 anything else?