... Male PVC adapter has straight threads and listed for enclosure connection.
....
On a male adapter, yes.Are you saying PVC threads are not tapered NPT threads?
On a male adapter, yes.
You just taught me something. After reading this post I went and picked one up off our shelf and sure enough.
Interesting.
There is a guy named Mark Ode who works for UL that explained this PVC threads into a hub thing in a paper/article.
I will see if I can find it if someone does not provide a link before I do. Opened a few eyes, mine included.
Example please. Most cases I've seen have tapered threads on both PVC gendered adapters.On a male adapter, yes.
Get an LB made for EMT.I've always ran in EMT connector into an lb. How else would you use an lb with EMT?
I've always ran in EMT connector into an lb. How else would you use an lb with EMT?
Get an LB made for EMT.
Is that acceptable in a wet location with raintight connectors in the setscrew LB?
NPSM male in NPSM female
Setscrews = mech/elec continuity
Gaskets = waterproofing
EMT conduit bodies do not have threaded entries.Is that acceptable in a wet location with raintight connectors in the setscrew LB?
I've always ran in EMT connector into an lb. How else would you use an lb with EMT?
Those threaded LBs with setscrews are combo devices. Can be used with either threaded conduit or EMT. The setscrew is for EMT, not to crank down on the pipe threads.
-Hal
Using any connector in a threaded entry is a listing violation.
Dunno about that. I didn't look up any conduit bodies but this is from the Raco/Bell catalog Bell box description: Hubs accept all threaded fittings and threaded conduit.
-Hal
Out of curiosity, I did verify that statement is on their data sheet and the boxes are UL listed. I'd have to research the entire chain of listings to say "I am wrong" for certain. The reason I assert using a connector (metal, with straight threads) is a listing violation is because the UL Whitebook states something to the effect that fittings with straight threads inserted into hubs with tapered threads have not been investigated to provide adequate grounding. It has been a few, perhaps several years, so perhaps it has changed. Anyone know?Dunno about that. I didn't look up any conduit bodies but this is from the Raco/Bell catalog Bell box description: Hubs accept all threaded fittings and threaded conduit.
-Hal