Meyers/TA pvc

Status
Not open for further replies.
Not compliant with listings. Meyers hub is only listed for use with RMC/IMC. Male PVC adapter has straight threads and listed for enclosure connection.

To be compliant, put a rigid close nipple in the Meyers and a female PVC adapter on the nipple.
 
You just taught me something. After reading this post I went and picked one up off our shelf and sure enough.
Interesting.

There is a guy named Mark Ode who works for UL that explained this PVC threads into a hub thing in a paper/article.

I will see if I can find it if someone does not provide a link before I do. Opened a few eyes, mine included.
 
Is that acceptable in a wet location with raintight connectors in the setscrew LB?
EMT conduit bodies do not have threaded entries.

There are combination RMC, IMC, EMT conduit bodies with threaded entries, but they are only listed for wet locations when used with RMC, perhaps IMC.

Using any connector with straight threads in a threaded entry is a listing violation. There are some (very few) connectors made and listed that have NPT threads that you can use, but typical connectors have straight threads.
 
Those threaded LBs with setscrews are combo devices. Can be used with either threaded conduit or EMT. The setscrew is for EMT, not to crank down on the pipe threads.

I've always ran in EMT connector into an lb. How else would you use an lb with EMT?

Use a raintight compression EMT connector with sealant same as you would with a Bell box. That's all you can do and it's compliant. However if this were a really wet location (like exposed to rain or washdown) I wouldn't use EMT to begin with.

-Hal
 
Using any connector in a threaded entry is a listing violation.

Dunno about that. I didn't look up any conduit bodies but this is from the Raco/Bell catalog Bell box description: Hubs accept all threaded fittings and threaded conduit.

-Hal
 
Dunno about that. I didn't look up any conduit bodies but this is from the Raco/Bell catalog Bell box description: Hubs accept all threaded fittings and threaded conduit.

-Hal

If you are quoting Smart$, then that is not what he wrote. You edited it and that is misleading.

He wrote:

Using any connector with straight threads in a threaded entry is a listing violation.
 
Dunno about that. I didn't look up any conduit bodies but this is from the Raco/Bell catalog Bell box description: Hubs accept all threaded fittings and threaded conduit.

-Hal
Out of curiosity, I did verify that statement is on their data sheet and the boxes are UL listed. I'd have to research the entire chain of listings to say "I am wrong" for certain. The reason I assert using a connector (metal, with straight threads) is a listing violation is because the UL Whitebook states something to the effect that fittings with straight threads inserted into hubs with tapered threads have not been investigated to provide adequate grounding. It has been a few, perhaps several years, so perhaps it has changed. Anyone know?

Oh, BTW, the reason I mentioned straight threads on a PVC male adapter wasn't because of grounding (obviously). Rather that's about retaining a wet location rating for the enclosure. While PVC itself is wet location rated, you'd have to use a sealing washer or sealing locknut to maintain a wet location rating for the enclosure... and that would only be compliant when connecting directly to the enclosure... so there's no purpose for using a Myers hub.
 