On a medium voltage customer-owned MGN system, can you use the neutral as the method to ground equipment? Or do you have to run separate EGCs?
Electrically, I feel like I could make an argument for either way. The separate EGC is pointless because it's directly in parallel with the neutral and could carry current in normal conditions. Or the separate EGC is a good idea because it ensures continuity between metallic components (even though it would be there anyway).
Envision some MV gear fed from utility MGN feed. N-G share a common bus in this gear and there exists GEC to ground rods, then what wires would you need to bring from the gear to a YgYg transformer?
250.190(A) Kind of makes me think that I could use neutral as grounding method.
Part X of article 250 leaves some clarity to be desired...
Electrically, I feel like I could make an argument for either way. The separate EGC is pointless because it's directly in parallel with the neutral and could carry current in normal conditions. Or the separate EGC is a good idea because it ensures continuity between metallic components (even though it would be there anyway).
Envision some MV gear fed from utility MGN feed. N-G share a common bus in this gear and there exists GEC to ground rods, then what wires would you need to bring from the gear to a YgYg transformer?
250.190(A) Kind of makes me think that I could use neutral as grounding method.
It simply says "shall be grounded". Well if we're talking about the transformer, and the neutral is being grounded there again, then connecting to the neutral certainly seems logical to say it is being grounded.250.190 Grounding of Equipment.
(A) Equipment Grounding. All non–current-carrying metal
parts of fixed, portable, and mobile equipment and associated
fences, housings, enclosures, and supporting structures shall be
grounded
Part X of article 250 leaves some clarity to be desired...