So pipe and wire no more than 360 bend w/o pull point/box.
What happens if you have horizontal run 1/C MI with 9-10 bends?
How is that pull handles as far as splice/pull points(I know it's not wire)/boxes?? Thanks
 
MI cable has no limits on the number of bends because you are not pulling conductors in after it's installed.
 
Status