mstrlucky74
Senior Member
- Location
- NJ
Would you use the same size wire when switching from MI Cable to pipe and wire(thhn)? According to this pic and the 200A breaker and ATS seems like I can use smaller wire than 3/0 it's showing for the MI Cable. Even with voltage drops it looks like I can use 1/0 or 2/0 not 3/0 as shown with the MI cable.
Distance is about 160' away.
Thanks.
Distance is about 160' away.
Thanks.