D douglas11 Member Jan 16, 2009 #1 what to know if u have to splice mi cable what kind of juction does it have to be,can it be i regular jb or special fire rated one
what to know if u have to splice mi cable what kind of juction does it have to be,can it be i regular jb or special fire rated one
B benaround Senior Member Location Arizona Jan 16, 2009 #2 Douglas, I guess that would depend on the location.
V Volta Senior Member Location Columbus, Ohio Jan 16, 2009 #3 300.15(D) Type MI - None if accessible fittings. If you are usng it for the fire-rating characteristics then the fitting should be rated so also, I presume. Welcome to the forum.