A Alwayslearningelec Senior Member Location NJ Occupation Estimator Dec 13, 2023 #1 Anyone familiar with this and the pyropak kits? Do you need ot transition to THHN etc. when terminating?
Anyone familiar with this and the pyropak kits? Do you need ot transition to THHN etc. when terminating?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Dec 13, 2023 #2 Is this in a hazardous location?
A Alwayslearningelec Senior Member Location NJ Occupation Estimator Dec 13, 2023 #3 infinity said: Is this in a hazardous location? Click to expand... No. why?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Dec 13, 2023 #4 It appears you terminate the conductors of the MI directly to the equipment or a terminal block. https://go.nvent.com/rs/760-EGW-100/images/Pyrotenax-IM-H58872-PyropakTermination-EN.pdf
It appears you terminate the conductors of the MI directly to the equipment or a terminal block. https://go.nvent.com/rs/760-EGW-100/images/Pyrotenax-IM-H58872-PyropakTermination-EN.pdf