Michigan questions

Status
Not open for further replies.

rondo

New member
Adding a stick built addition to an existing mobile and have a couple of questions on the "field correction notice" received regarding the rough electrical inspection.

1) Uncorrected
R109.1.5 (MI residential code?)
Make up wires in electrical boxes.

I can't get hold of the inspector (on vacation) and I don't see that term used anywhere. Any idea what it means?

2) Uncorrected
E3303.3 and NEC 550.32(D)
Branch circuits outside of trailer shall originate at trailer service panel.

550.32(D) doesn't state that and I'm not sure if they are saying that they have to be dedicated circuits (which would be news to me), but again, any ideas?

I appreciate any help. The wiring was completed by a family member (Local 58) and he's done residential before without a hitch. I'm really kind of thrown by the description of the "problems" and was curious if it's common language, or not.
 
Re: Michigan questions

550.32(D): Additional Outside Electrical Equipment Means for connecting a mobile home accessory building or structure or additional electrical equipment located outside a mobile home by a fixed wiring method shall be provided in either the mobile home service equipment or the local external disconnecting means permitted in 550.32(A)

My guess is the service is located adjacent to the mobile home. If this addition requires a fixed wiring method (which I assume it does), he is saying that because the service equipment has to provide for a means of connecting accesssory building or structure you are required to use it.

As far as the other violation. I am guessing without looking at it that he wants good work practices followed and have all splices made in boxes before rough inspection.
 