Wanted to see if my reasoning is correct on this one.
In the State of Michigan, is the requirement of 210.8(B)(5) mandated for a dwelling unit air conditioner?
210.8(B)(5) points to 210.63 which points back to 210.8 for GFCI requirements in a FPN.
Michigan code, Part 8, rule 801 states, in part:
Rule 801. National electrical code; adoption by reference; inspection;
purchase.
The standards contained in the national electrical code, 2005 edition, except
sections 501.30B, 502.30B, 503.30B, 505.25B, 506.25B, 547.1 to 547.10, and
Annex G, as published by the national fire protection association, shall govern the
installation, replacement, alteration, relocation, and use of electrical systems or
material. With the exceptions noted, the national electrical code is adopted in these
rules by reference. Fine print notes contained within the body of the code are not
adopted as a part of the code. All references to the ANSI/ASME A17.1 2004, Safety
Code for Elevators and Escalators means the Michigan Elevator Code and all
references to the National Electrical Code means the Michigan Electrical Code. The
code is available for inspection at the Okemos office of the Michigan department of
labor and economic growth, bureau of construction codes.
I am assuming that this means that 210.8 does not apply to a receptacle for a dwelling unit air conditioner per michigan code. Any flaws in my logic?
This seems so simple, but for some reason I keep going back to it.
Thanks
In the State of Michigan, is the requirement of 210.8(B)(5) mandated for a dwelling unit air conditioner?
210.8(B)(5) points to 210.63 which points back to 210.8 for GFCI requirements in a FPN.
Michigan code, Part 8, rule 801 states, in part:
Rule 801. National electrical code; adoption by reference; inspection;
purchase.
The standards contained in the national electrical code, 2005 edition, except
sections 501.30B, 502.30B, 503.30B, 505.25B, 506.25B, 547.1 to 547.10, and
Annex G, as published by the national fire protection association, shall govern the
installation, replacement, alteration, relocation, and use of electrical systems or
material. With the exceptions noted, the national electrical code is adopted in these
rules by reference. Fine print notes contained within the body of the code are not
adopted as a part of the code. All references to the ANSI/ASME A17.1 2004, Safety
Code for Elevators and Escalators means the Michigan Elevator Code and all
references to the National Electrical Code means the Michigan Electrical Code. The
code is available for inspection at the Okemos office of the Michigan department of
labor and economic growth, bureau of construction codes.
I am assuming that this means that 210.8 does not apply to a receptacle for a dwelling unit air conditioner per michigan code. Any flaws in my logic?
This seems so simple, but for some reason I keep going back to it.
Thanks