Micro Shock
mbrooke
Batteries Included
United States
Technician
Is code mandated grounding and bonding enough to stop micro shocks? Can standing neutral to ground faults cause them?
Yes, and no.
1. Phase to ground shorts can elevate the neutral and ultimately through the resistance of the POCO service neutral and the GES if a local earth ground is accessible (such as water pipes, structural steel, etc., even when NEC mandated grounding and bonding rules are followed.
2. Phase to neutral shorts can cause microshock potentials IF NEC grounding and bonding standards are not followed, AND can cause microshock potentials even when NEC mandates are followed if the entire service neutral voltage is raised, elevating the ECG potential to distant earth at the same time. The microshock risk occurs when a different source of local ground is accessible, such as via water pipes, structural steel, concrete floors, etc.
3. The specific bonding standards for pools are designed to eliminate (or greatly reduce) the chance of microshock potential differences from any offset of bond system potential from distant earth/EGC potential, regardless of the source. Other areas of buildings and yards do not have that extra equipotential bonding of all surfaces which can be touched, including local dirt.
4. All of the above risks can be mitigated by proper overcurrent and ground fault protection.
Regarding #2, doesn't the NEC as written eliminate all remote earth points in an OR?
In general- my understanding is that during a fault the EGC will become a resistive divider- making for voltage differences within the bonding system itself? Over current and GF would shorten that duration.
One other issue is that the health effects of 'microshocks' are unclear.
The image in the OP states a maximum safe threshold of 10uA, well below the threshold of sensation. GFCIs trip at 600x this level.
There has been research into the health effects of 'contact current' as a possible mechanism for the (possible but not proven) association of 'EMF' exposure and leukemia. If you want to explore this you will need to wade through a bunch of EMF woo. (I believe that there is a real possibility of non-thermal effects from EMF exposure, but there is a huge amount of bs and fear mongering in any discussion of such, so I don't spen much time on it.)
-Jon
-Jon
Rather worse than that- it takes micro amps to send the heart into fibrillation. At least what Mike Holt taught me.
The article does not mention the requirement of the equipotential in patient care rooms to be less than 0.1 ohm which solves the problem of multiple earth points. This equipotential must be tested with apparatus as shown in annex A of NFPA 99 prior to commissioning the room(s) and periodically there after.
Roger
If you are talking whole body shock, eg from an arm to a leg via the torso, then the current expected to cause fibrillation is in the 10s of milliamps.
I bet you wouldn't even feel a 10 microamp current from hand to foot.
I can believe the number is much lower if you are talking of a patient care scenario with direct electrical connection to the heart.
-Jon
Roger
This
Roger
-Jon
Agreed. Remember though that the body is a near infinite number of resistors in series parellel (mesh). 50ma hand to foot would be much less across the heart.