17-21 Log #219 NEC-P17 (422-16(B)(4) (New) )
Final Action: Accept in Principle in Part
Submitter: Don A. Hursey, Durham County Inspections Department
Recommendation:
Add new text to read as follows:
Permanently installed range hoods shall be permitted to be permanently connected or cord and plug connected.
Substantiation:
Many times range hoods are removed and replaced with a "microwave type" range hood. Allowing cord and plug connection will make the installation much easier for the homeowner because no "electrical change" to the wiring system will be required.
Panel Meeting Action: Accept in Principle in Part
Add a new section to read as follows:
422.16(B)(6) Range Hoods. Range hoods shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the use on range hoods in the installation instructions of the appliance manufacturer, where all of the following conditions are met.
(1) The flexible cord shall be terminated with a grounding type attachment plug.
Exception: A listed range hood distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall not be less than 450 mm (18 in.) and not over 900 mm (36 in.).
(3) Receptacles shall be located to avoid physical damage to the flexible cord.
(4) The receptacle shall be accessible.
(5) The receptacle shall be supplied by an individual branch circuit.
Panel Statement:
The permission to use cord-and-plug connection provides the ability to upgrade to a combined microwave range hood. The panel added the additional requirements to ensure a safe installation of a combined microwave range hood.
Number Eligible to Vote: 12
Affirmative: 12