jeff48356
Senior Member
- Location
- Livonia, Michigan
Just wondering how many of these types of calls you all get. I get these quite frequently, with the latest being today. I see this scenario far too often: Someone has their kitchen remodeled, which originally had a range hood over the stove. The customer wants a built-in microwave oven installed in its place. So the remodelers, who have no business doing electrical work, take the 14-2 cable from the range hood and use it to power an outlet in the cabinet for a microwave. The customer uses the microwave while other loads on the circuit are being used, and the breaker trips every time. So they call me to figure out what's going on. I determine that to be the cause, then end up running a new 20A circuit from that outlet to the breaker panel -- what should have been done during the renovation in the first place. When are people going to understand that you CANNOT run a microwave oven off a 15A lighting circuit without popping a breaker??