ptonsparky
Tom
- Occupation
- EC - retired
CH VFD for a customer failed to start yesterday. Showed a fault that indicated either the motor load was wrong or an IGBT failure. The guys megged the motor and wires. No faults P-P or P-G with resistance of windings entirely within expectations. New AB drive went on this morning and immediately showed fault code of U-V. They called for help and we cussed & discussed the tests again. I had them repeat everything while I drove out. Naturally the first disconnect I open I find a phase wire that obviously, because I looked closely, has seen an intermittent fault to ground. We installed it. The miffed part. They removed all the wiring and pulled new without finding an additional fault. They are bringing the wire back to the shop so we can examine it closely. Old drive went back in and everything is fine. Puzzled why the drive showed a load side fault between conductors and not a ground fault. (Granted I may not be puzzled if I find other damage.) Basically a no charge day with a new AB VFD on hand that I don't need. Another miffed part.