factoryrat
Member
- Location
- Detroit
I have three Miller Invision 354 MP DC Inverter Arc Welders. Input Voltage 460 V, 3-phase. The nameplate says: INPUT = 11.5kw and 18.9 amps. How do I calculate OCPD size and wire size if I want to put all three welders on one circuit? And what size OCPD and wire size would be needed if I was to run an individual circuit to each mig welder?
I have an existing 60A circuit (OCPD = 60A & feeder wire size is #6) not being used for anything else. I have one of the three new welders hooked up to this circuit now. There is a fused disconnect at the welder which is fused at 40A. I was wondering if from the existing 60A circuit I can connect the other two mig welders?
With these new welders I received an owner?s manual. The manual has a page that shows a table. I believe the table indicates each one of the welders should be protected by 15A Time-Delay fuses. This seems small to me and because I do not know how to calculate the correct sizes I'm confused. If I am reading this right ? Can I use the 60A feed and run it to each welder where I?d have a disconnect with 15A fuses to protect the mig welder?
Believe it or not I am an electrician but have never calculated circuit protection for mig welders before. I would appreciate any information anyone could give. Thank you.
I have an existing 60A circuit (OCPD = 60A & feeder wire size is #6) not being used for anything else. I have one of the three new welders hooked up to this circuit now. There is a fused disconnect at the welder which is fused at 40A. I was wondering if from the existing 60A circuit I can connect the other two mig welders?
With these new welders I received an owner?s manual. The manual has a page that shows a table. I believe the table indicates each one of the welders should be protected by 15A Time-Delay fuses. This seems small to me and because I do not know how to calculate the correct sizes I'm confused. If I am reading this right ? Can I use the 60A feed and run it to each welder where I?d have a disconnect with 15A fuses to protect the mig welder?
Believe it or not I am an electrician but have never calculated circuit protection for mig welders before. I would appreciate any information anyone could give. Thank you.