What size wire you need if you daisy chained the MIGB together and size if you did it individually to the enclosure
What kind of circuit is it?500 mcm
Metallic insulated grounding bushing.What is MIGB?
Is a 3 phase disconnectWhat kind of circuit is it?
MIGB is a malleable insulation grounding bushingWhat is MIGB?
If it's a feeder then the bonding jumper is sized according to the OCPD ahead of the feeder from T250.122.Is a 3 phase disconnect
So if I have a 600 amp then my daisychained My MIGB with a 2/0 aluminum.If it's a feeder then the bonding jumper is sized according to the OCPD ahead of the feeder from T250.122.
Yes #2/0 AL is the correct size. You can use individual bonding jumpers from each raceway or loop a single conductor through all of the bonding bushings.So if I have a 600 amp then my daisychained My MIGB with a 2/0 aluminum.
Thank you for your helpYes #2/0 AL is the correct size. You can use individual bonding jumpers from each raceway or loop a single conductor through all of the bonding bushings.
Metallic insulated grounding bushing.
Which one is it!MIGB is a malleable insulation grounding bushing
Metallic insulated grounding bushingWhich one is it!
There is two different size if I Daisychain them what’s the code 250.122.Thank you for your help
It sounds like you are referring to service conductors which does not use 250.122 but rather 250.102 and daisy chaining will require different sizing. Different sizes will not happen on a feeder when daisy chaining and 250.122 applies. What are these conductors?There is two different size if I Daisychain them what’s the code 250.122.