So if I have a 600 amp then my daisychained My MIGB with a 2/0 aluminum.
Yes #2/0 AL is the correct size. You can use individual bonding jumpers from each raceway or loop a single conductor through all of the bonding bushings.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
There is two different size if I Daisychain them what’s the code 250.122.
It sounds like you are referring to service conductors which does not use 250.122 but rather 250.102 and daisy chaining will require different sizing. Different sizes will not happen on a feeder when daisy chaining and 250.122 applies. What are these conductors?
 