MIGB

Status
Not open for further replies.
Lets' start with why you're installing one in the first place? There are many variables and they're actually not required by the NEC very often. Having said that I see them installed all over the place when not required.
 
Hey Inf. Just came across this. I think you said in another post they are required when terminating conduit into a box with KO when the voltage id 277 or higher?
 
Hey Inf. Just came across this. I think you said in another post they are required when terminating conduit into a box with KO when the voltage id 277 or higher?
I beleive I stated that when the raceway enters through a concentric or eccentric KO and the voltage is above 250 volts to ground a bonding bushing is required.
 
Usually just on one end. However there are situations where you would need one on each end. Follow the fault current: can it get back to the source without having to go thru a KO (for over 250v to ground) or a regular locknut (for supply side)? For example consider on the supply side of the service disconnect, a pull box nippled into a service disconnect cabinet. You could bond the pull box to the neutral, use a SSBJ from the pull box to the neutral bus in the service disconnect, or you could bond it with the nipple but you would need a MIGB on each end.
 
Excuse my ignorance - what is MIGB? I'm sure it isn't Molybdenum Inverse Grease Barbiturates......................:)
 