Mike Holt Electrical Exam Prep Question 2017

Status
Not open for further replies.

sokbok

Member
Location
Kansas City
I am studying for my masters using the 2017 electrical exam prep book.

I am confused about the two examples on page 272. Specifically, how was the size
of the neutral determined for the Feeder calculations? Figures 6-71 and 6-72.

After reviewing 215.2A and 110.14C2 I am stumped on how the neutral can be
less than 100% of the possible unbalanced loads.

On the next page, figure 6-73, the
neutral is sized in what I think is the correct fashion.

Any help appreciated.:dunce:
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Mike sells his products on his website. This forum can be accessed from his website but we (forum members & mods) have no way of looking at the material. So we can't help with your problem/question unless you post a copy of what you are talking about.

I would suggest you contact the staff at Mike Holt's office. They will be able to help you with their material. Some years ago I used some of his material for exam prep and had to contact them a few times. They were always helpful with whatever I asked.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
He did not talk about the actual neutral load calculation in those two figures. He just said the neutral was sized at 100% of the neutral load. With the information given, there is no way to actually calculate the neutral load. You have no way of knowing how many 3 phase, line to line loads are being served by that panel. i believe that the point he is making there is that for continuous loads, you have to size the ungrounded conductors at 125% of the load, but the neural is sized at 100%.
 

sokbok

Member
Location
Kansas City
He did not talk about the actual neutral load calculation in those two figures. He just said the neutral was sized at 100% of the neutral load. With the information given, there is no way to actually calculate the neutral load. You have no way of knowing how many 3 phase, line to line loads are being served by that panel. i believe that the point he is making there is that for continuous loads, you have to size the ungrounded conductors at 125% of the load, but the neural is sized at 100%.

thank you very much. I was confused.
 