I recently read the above noted newsletter and it has me confused. Per 400.8.(6), you can't put a flexable cord in raceway but per 400.14, you can put them in raceway above grade. When designing pump stations and related projects, we would call for junction boxes to be placed outside the wet well and convert the pump cords and float cords over to hard wire that we can put in a duct bank back to the pump control panel. It was always our interpretation that the pump cords, float cords, and transducer cords were considered flexible cords and could not be installed in below grade raceway. Even if you search the forum, that appears to be the consensus.
However, after reading the newsletter, I am questing if these are indeed a flexible cords. Here are several questions:
1. Are the submersible pump cables, transducer cables, and float cables actually "power supply cords" or a "cord sets" constructed per UL817?
2. Where does article 400 state that the NEC is not applicable if the cords are UL 817?
3. So if the noted cables are built per UL 817, does it need to state it on the cable someplace?
4. If the cords are indeed UL817, can they be put in a duct bank?
Thoughts?
However, after reading the newsletter, I am questing if these are indeed a flexible cords. Here are several questions:
1. Are the submersible pump cables, transducer cables, and float cables actually "power supply cords" or a "cord sets" constructed per UL817?
2. Where does article 400 state that the NEC is not applicable if the cords are UL 817?
3. So if the noted cables are built per UL 817, does it need to state it on the cable someplace?
4. If the cords are indeed UL817, can they be put in a duct bank?
Thoughts?