when using MIkes Holts residential load calculator. once you plug in sq ft, small appliance, and laundry circuit, and after you insert other things such as diswasher disposal trash compactor etc etc would adding any other circuits other than ones discribed add to load calculations final load demand for calulating service. im a little tired and sleepy hope this makes sense
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
when using MIkes Holts residential load calculator. once you plug in sq ft, small appliance, and laundry circuit, and after you insert other things such as diswasher disposal trash compactor etc etc would adding any other circuits other than ones discribed add to load calculations final load demand for calulating service. im a little tired and sleepy hope this makes sense

Could you be more specific about what "other loads" you are talking about?

If its small plug in appliances, then the general receptacle loads may have it covered.

If you are talking about larger or hardwired items, I'd say yes, that needs to be added into the load calcs.
 