I'm going through the calculations section of this test and I need help determining when to use the 60° column and when to use the 75° column for sizing conductors/OC device for welders.
At first I was following 110.14(C)(1) for under 100A with no terminal listing use 60°
I then ran into another question that the load was under a 100A , however the answer given used the 75° column
Question 36
A nonmotor generator arc welder has primary current rating of 40A with duty cycle of 50%. The branch circuit conductor for the welder must be rated at least _______
Answer is 30A based on 60°
Question 38
The maximum OC device rating for 10AWG conductors used for arc welder branch circuit is ______
Answer is 70A based on 75°
Does it state which degree column to use based under conditions?
Thanks for the help!
Sent from my SM-G950U using Tapatalk