"Well-grounded principles" dated June 27, 2007 talks about the guidelines how to eliminate lightning damage with proper grounding.
Mike Holt had comments on Ufer ground. One of his comments was
He also said,
He goes on and said,
I guess I am still not sure how a grounding electrode requred by the NEC is different from a grounding electrode as requred by NFPA 780.
How does the grounding electrod provide a path for inducted overvoltage to the earth?
Mike Holt had comments on Ufer ground. One of his comments was
NEC equipment grounding electrode are not intended to serve as the lightning protection grounding electrode.
He also said,
The study published in the IEEE August 1970 by Mr. Eugene J. Fagan and Mr. Ralph Lee evaluated steel rebar in concrete as a suitable 'grounding electrode.' Note: A grounding electrode as required by the NEC is not for lightning protection, so the study evaluated the rebar/concrete for surge and fault current, not lightning.
Summary, steel rebar is an excellent electrode as required by the NEC, but it is not permitted by NFPA Lightning Protection Code to be use as the lightning protection electrode.
He goes on and said,
A grounding electrode as per the NEC is to provide a path for inducted overvoltage to travel to the earth. Not a direct lightning strike.
I guess I am still not sure how a grounding electrode requred by the NEC is different from a grounding electrode as requred by NFPA 780.
How does the grounding electrod provide a path for inducted overvoltage to the earth?