Vonn Mann
New member
- Location
- Ellisville, MO, USA
When using Mike Holt short circuit calculator, City Utility Company tells me to use 10000amps for input into Utility Fault Current at the transformer. This means that all panels beyond this on the electrical circuit will be less than 10000amps. So 10kva Short Circuit Current Rating on electric panels would be adequate. How does City Utility company set the Utility Fault Current to only be 10000amps? So for example: 150kva transformer, 1.6% impedence, 208v, 3phase service. I, Current at transformer is 150kva x 1000 / sqrt3 x 208v = 416 amps. I, Short Circuit at transfomer is 416amps / 0.016 = 26025amps. How does City Utility Company set the Fault Current at 10000amps? Instead of the calculated 26025 amps. Please help me understand this. Thankyou. Vonn