I was just reading the Mike Holt?s newsletter from yesterday and item 14. (?The flexible connection to emergency system equipment in hospitals?) is something I?ve seen allowed in my area. Part of the commentary reads:
?The intent is clear that it is only permitted "where necessary" not where convenient, possible, preferred or easier! The option to use a flexible wiring method would have to be "identified" as "necessary" where it relates to the connection of the equipment and "approved" by both State and Local Authorities Having Jurisdiction. If the intention to use a flexible wiring method in this application to connect emergency luminaires is for reasons of convenience, preference, ease of installation, or financial, it is not considered "NECESSARY!"? (see www.nh.gov/electrician/14_2005.html for the complete commentary and code references)
I have never had an inspector point this out and not allow flex to emergency fixtures. I?m curious if other AHJ interpret it the same way?
?The intent is clear that it is only permitted "where necessary" not where convenient, possible, preferred or easier! The option to use a flexible wiring method would have to be "identified" as "necessary" where it relates to the connection of the equipment and "approved" by both State and Local Authorities Having Jurisdiction. If the intention to use a flexible wiring method in this application to connect emergency luminaires is for reasons of convenience, preference, ease of installation, or financial, it is not considered "NECESSARY!"? (see www.nh.gov/electrician/14_2005.html for the complete commentary and code references)