Milbank recall!

Status
Not open for further replies.

Mgraw

Senior Member
Location
Opelousas, Louisiana
Occupation
Electrician
"The recalled model number 9090 appears on the right or left side of the installed meter socket. If not installed, model numbers U9090-O or R9090-O will appear on the label on the outside of the box.
Sold at: Electrical supply distributors in N.Y., Pa., Vt. and Mass. and at local hardware stores in N.Y. from May 2009 through August 2009"
 

A-1Sparky

Senior Member
Location
Vermont
Yeah, I heard that from my supplier. Supposedly, many of the cans that were shipped out had continuity between the ungrounded conductor lugs and the enclosure. Another reason to always check for continuity before installation and energization.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
This manufacturer mis-assembly (a "bridge" support that is too short that mounts the meter jaws close to the front of the enclosure) looks like, if one shoves a meter movement into the meter jaws, the short bridge doesn't push back, 'cause its not against the back of the enclosure. The pressure of pushing the meter into it's jaws bends the bus bars coming from the line lugs beneath the jaws, and the bolted upper end of those bus bars might, in fact touch the enclosure.

Looks like one could even get a 240 V short through the pan.
 