Have been ask to connect a 60 Kw 3 phase military generator to a rural fire department building with a manual transfer switch. The name plate has it at 208 amps at 120/208v. I will be connecting it single phase since the building is 120/240 v 1 ph. My question is because I am using only 2 of the phases, that beats out to 138 amps. So do I size the wire and over current to that or will I have to size per the name plate even though I am not using all 3 phases? The generator doesn't have OC protection so I know I will have to size the wire at 115% to the disconnect per 445.13. So by this my conductors from the generator to the disco. would have to be 2/0 with 160 amps fuses. Or am I going to have to size 115% of the name plate 208 amps?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Most of the military generators I have seen were 12 lead and could be reconnected for 120/240 single phase at 2/3s the rated KVA. The connection is called a zig-zag connection at I recall. So at 40kw, 120/240, the current would be 166.6.

That being said, I think the answer to your question is that the conductors are sized based on the current that the generator can supply to the conductors.
 

ceb58

Senior Member
Location
Raeford, NC
Most of the military generators I have seen were 12 lead and could be reconnected for 120/240 single phase at 2/3s the rated KVA. The connection is called a zig-zag connection at I recall. So at 40kw, 120/240, the current would be 166.6.

That being said, I think the answer to your question is that the conductors are sized based on the current that the generator can supply to the conductors.

Looked at it, only 2 voltages available 120/208 or 240/316
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Looked at it, only 2 voltages available 120/208 or 240/316
Is that from the nameplate? Some of the ones I worked on only had a couple of voltages on the nameplate, but they were 12 lead generators, and the manual gave the connections for the other voltages. If it is only a 9 lead machine, you are stuck with the two nameplate voltages.
 

ceb58

Senior Member
Location
Raeford, NC
Is that from the nameplate? Some of the ones I worked on only had a couple of voltages on the nameplate, but they were 12 lead generators, and the manual gave the connections for the other voltages. If it is only a 9 lead machine, you are stuck with the two nameplate voltages.

Nine lead. Looked at the lead connection board. So it looks as if I'm at 192 amps @ 208
 

kwired

Electron manager
Location
NE Nebraska
Looked at it, only 2 voltages available 120/208 or 240/316
240/316 or 240/416? 240/416 is possible with a wye connection 240/316 is not.


add: 120/208 to 240/416 change is possible with a nine lead generator, low voltage connection is two parallel wye sets, high voltage puts three outer sections of the wye in series with the inner 7-8-9 leads. To be able to get 277/480 out of this you need to do some tweaking of the regulation methods when switching voltages.
 
Last edited:

ceb58

Senior Member
Location
Raeford, NC
240/316 or 240/416? 240/416 is possible with a wye connection 240/316 is not.


add: 120/208 to 240/416 change is possible with a nine lead generator, low voltage connection is two parallel wye sets, high voltage puts three outer sections of the wye in series with the inner 7-8-9 leads. To be able to get 277/480 out of this you need to do some tweaking of the regulation methods when switching voltages.

316 was a type o . Will be going with the 120/208 voltage just using 2 legs instead of 3.
 