In a single unit within a new multi-family dwelling (apt), is there a minimum number of general purpose lighting/receptacle breakers required? 2008 NEC.
As near as I can tell you start with Table 220.12, in conjunction with 220.14(J)(1). Let's say we have a small studio apartment, 650 square feet. 650sf X 3VA/sf = 1950VA. Then per 220.10 branch circuit loads are calculated based on this number. So 1950VA / 120V = 16.25A.
Unless I am missing something, in this instance the whole general purpose lighting/receptacle breaker requirements can be covered with one 20A/1P circuit. Thoughts?
I know this will be asked...so I'll mention it now. The Developer is adament that we install to code minimum, which is certainly legal. They can deal with the complaints (if there are any). They have along history of operating their own apartments so I don't have to feel any guilt about this being passed on and not communicated to an unwitting future Owner.
Also, I realize there are many other breaker requirements - 2 for the kitchen, 1 for bathroom, 1 for laundry, any fixed-in-place equipment (fridge, range, hoods, washer, dryer, AC/furnace, etc). I'm fine limiting discussion to the general receptacles but feel free to check me.
Thanks!
As near as I can tell you start with Table 220.12, in conjunction with 220.14(J)(1). Let's say we have a small studio apartment, 650 square feet. 650sf X 3VA/sf = 1950VA. Then per 220.10 branch circuit loads are calculated based on this number. So 1950VA / 120V = 16.25A.
Unless I am missing something, in this instance the whole general purpose lighting/receptacle breaker requirements can be covered with one 20A/1P circuit. Thoughts?
I know this will be asked...so I'll mention it now. The Developer is adament that we install to code minimum, which is certainly legal. They can deal with the complaints (if there are any). They have along history of operating their own apartments so I don't have to feel any guilt about this being passed on and not communicated to an unwitting future Owner.
Also, I realize there are many other breaker requirements - 2 for the kitchen, 1 for bathroom, 1 for laundry, any fixed-in-place equipment (fridge, range, hoods, washer, dryer, AC/furnace, etc). I'm fine limiting discussion to the general receptacles but feel free to check me.
Thanks!