ultramegabob
Senior Member
- Location
- Indiana
what is the minimum size that a motor has to have overloads 120v, or could someone direct me to a chart online? I dont have any ref books with me, thanks....
augie47 said:I agree with Iceman on the reference to 430.32 and 430.33
I don't happen to agree with the FLA statement.
If the motor is Continuous duty and more than 1 HP, it needs OL protection.
If the motor is 1hp of less and automatically started it needs OL protection
If the motor is 1hp or less and non-automatically started and not permanently installed the branch circuit device may possibly serve as
OL (see 430.32D)
If the motor is intermittent or similair the branch circuit device might be the OL protection.
As you can see, there is no simple answer.
ultramegabob said:I think your answering my question, I have a .75 hp 120v motor contiuous duty manually started with a switch, #12 wire protected with 20 amp breaker, permanently installed in a exhaust fan.
augie47 said:then, the way I read NEC, it's permanently installed so 430.32(D) (1) will send you back to 430.32(B) and some type O.L. is needed.
Typically these installatiions have thermally protected motors (internal) or are protected by a "manual motor starter" resembling a wall switch.
augie47 said:unless the motor has integral theraml protection, I agree
cadpoint said:Spring for a Code Book !
ultramegabob said:If you read my first post, I stated that I dont have my books with me
JohnJ0906 said:http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=70&cookie_test=1
You can see the '02, '05' and '08 NECs from here.