winslowfam
Senior Member
- Location
- VA
Hi...I would like some clarification on motor circuit protector sizing. The code often refers to Art. 240.6 for standard breaker sizes, to be used for sizing circuit overcurrent protection. The smallest standard size breaker on that list is 15A, so I've always thought that for motor short circuit protection, the smallest breaker rating I needed to go to was 15A, even for small motors (like a 1/2 HP at 480V with 1.1FLA). In my recent reading of Art. 430 for Motor Circuit Protectors, there is no reference to Art. 240.6 for the MCP rating...just directions on how to calculate the MCP rating based on motor FLA. There are even some handy motor protection charts from vendors (Cutler Hammer, etc.) that specify a 15A breaker to protect a 1/2 HP motor, but their chart call for a inverse time breaker...not an MCP. Do you have any comments on this, on whether or not 15A is the smallest rating I would need to go to with an MCP to be code-complaint, or not? thanks.