Min sizing of Motor Termination Box per NEC and or MG-1

Dale001289

Senior Member
Location
Georgia
I've got a large induction 460V, 3Ph AC motor that is being fed by 3-1/C 600kCMIL cable. The motor term box from the Vendor seems to be vastly undersized. What is the best way to calculate the min size required
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
As infinity said, if the motor is a Listed device then NEC does not apply to its termination box.
If the motor is not listed the NEC should be used, as there is no other governing standard, as most of them, like MG-1, are voluntary.
 