IMO, not required. The disconnect at the condenser will kill power to the head.Does the indoor air handler of a mini split system require a separate disconnect or does the exterior compressor disconnect suffice?
Thank you
Thank you.I think the answer lies in 440.8: "An air-conditioning or refrigerating system shall be considered to be a single machine under the provisions of 430.87, Exception No. 1, and 430.112, Exception. The motors shall be permitted to be located remotely from each other."
So the indoor unit and the outdoor unit are a single machine, and it's fine that the indoor unit has a motor in it remote from the outdoor unit. Then 430.112 Exception (1) allows a single disconnect for the entire machine.
Cheers, Wayne
What if the indoor unit's fan was run from a completely separate circuit, rather than powered from the outside unit?So the indoor unit and the outdoor unit are a single machine, and it's fine that the indoor unit has a motor in it remote from the outdoor unit. Then 430.112 Exception (1) allows a single disconnect for the entire machine.
Same here. A lot of the newer units the indoor unit is NOT fed from the outdoor unit and require a 208/240v, single phase circuit and local disconnect.A lot of the ones i have recently install call for a local 2 pole switch or disconnect and also sometimes have had max fuse too.
Then if you wanted to use 440.8, your single disconnect would need to disconnect both circuits. Otherwise, you're back to having two disconnects.What if the indoor unit's fan was run from a completely separate circuit, rather than powered from the outside unit?