Mini Split Same MCA AND MOPD

Merry Christmas
Location
United States
Occupation
Electrical Apprentice
How can the max fuse be 15 even though the MCA is also 15? Doesn’t the current need to be less than 80% of the OCPD?
 

Attachments

  • 75399786244__3E547BC3-5290-437B-88B7-8C65F5C1D92E.jpeg
    75399786244__3E547BC3-5290-437B-88B7-8C65F5C1D92E.jpeg
    358.9 KB · Views: 36

OldSparks

Member
Location
Vacaville CA USA
Occupation
Retired: Electrician, Submarine Electronics (21 years), Potable water system maintenance boss (21 years).
The unit draws 9 amps. Nine is only 60% of fifteen. What is the issue?
 