Had a good discussion with the electrical inspector regarding the wiring of the Mini Split heating/cooling systems that seen to be so popular in this area. Stated in the manufactures electrical installation guidelines, this unit requires a 20A 240V branch circuit to the outdoor unit and then states a 14-3 needed to be installed from the outdoor unit to the indoor unit. A weatherproof fused disconnect (20 amp fuses) is installed next to the outdoor unit. One inspector says that a 12-3 needs to be installed between the units, not the 14-3 wiring that the manufacture calls out for. The other inspector says the 14-3 is fine. After looking at the wiring schematic of the units, I see no 15 amp overload protection in the outdoor unit for the 14-3 wiring running to the indoor unit. Any thoughts on this? Thanks in advance.