goldbergma8
New member
- Location
- cincinnati, ohio
We are installing a 115volt minisplit heat pump in our building and our quote from an electrician does not seem right. Our electrical panel is 250 feet away from where the mini split will be installed but the electrician only stated he will use 3 (hot,neutral, and ground) 10AWG THHN wire in conduit. From my calculations, that will end up having 7.8% voltage drop. Is this ok? I figured we would need 6AWG to keep the voltage drop at a reasonable amount. Its a long wire run so I dont want the electrician to do the job then have the system fail or have the wiring start a fire. The minisplit specs are: 115volt, 60Hz, 1 phase, .7Amps (fan motor), 9.5 amps(compressor), 15amp min circuit ampacity, and 20Amp Max fuse.