pkhanan
Member
- Location
- Grass Valley, CA.
I am taking over a new construction 1200 s/f single family dwelling that is nearly complete. The (exterior mounted) panelboard is fed from a 200 amp service located 230 away on the "main house". At the main house 200 amp service entrance, a 100 amp breaker feeds 2 #4 Copper conductors through 2" PVC conduit. The conduit also house a #6 neutral and a #8 ground. The demand load for the new house is only 42 amps (all gas appliances). When I perform a voltage drop calculation, I find I that at 260' feet, the voltage loss for the #4 conductors to be about 3.11%
Assuming all that to be correct, and that the voltage drop is within an acceptable range, can I install a 50 amp breaker (at the main house panel) to supply the new dwelling or does NEC 230.79 (c) imply that I must supply the new dwelling with 100 amps?