malachi constant
- Minneapolis
Hi all,
A colleague asked me to help him answer this question. He specified a 30A/3P breaker for a 7.5HP 208V/3P fan motor. He asked me what I typically specify. My answer is:
* Refer to Table 430.250 for FLA -> 24.2A
* Multiply FLA x 125% -> 30.25A
* Round up to nearest breaker/fuse size -> 35A
I know 220.5 allows you to round down fractions of an amp (under 0.5), but not convinced that applies to motor protection.
I believe this is for a project where the 30A breaker is already purchased and in the field, so the question is do they need a larger breaker. I am advising "yes, unless someone can prove to me it is OK to round down".