jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
From an NEC perspective, there isn't much guidance on sizing a transformer and what value to use (i.e. article 220 vs actual) In fact, there isn't even anything other than 110.3 that says you can't overload a transformer (although 450.3 puts an indirect limit on it). I think that mca/next size up from mca is probably good practice, but I also think one could go a little lower code compliantly.
I agree. No real guidance.
Like using this thread as an example. MCA-24A, we will use 240V. 5760VA.
Do you spec a 6kVA or a 9kVA?