Using NEC 2011.
I noticed almost all 120V branch circuits use 2#12 AWG with another #12G. Is #12 used because the OCPD is a 20-amp breaker feeding a 20-amp receptacle? If that is the case, can I use #14 for feeding a 15A GFI so long as I use a 15A breaker in the panelboard? I don't see any reason why not..
How about a small (<1HP) motor operating at 230V, 3-ph? We always use #12 minimum, regardless of the OCPD (which could be a 15A MCP or even a 7A MCP). I can't seem to find the requirement in Article 310. Although I did find according with 430.22(G), #14 is permitted.
Any insights are appreciated.
Brandon