Minimum Cover Requirements, Table 300.50

Status
Not open for further replies.
When using Table 300.50, in a 19.9/34.5kV three phase circuit, what is understood as the circuit voltage? Is it the voltage of ungrounded conductor to ground (19.9kV)? Or is it the the voltage between phase conductors (34.5kV)?

Also, if I want to install RNC under a building slab, does column 4 (4 inches) prevail over column 2 (18 or 24 inches)?
 
Thank you moderator, Manuel 300.5 is my area. When I read 300.50 IMO column 4 would be your application.
 
manuel bonilla said:
Is it the voltage of ungrounded conductor to ground (19.9kV)? Or is it the the voltage between phase conductors (34.5kV)?
My best friend who is an EE in HV and MV distribution, says that system voltage is always given as the line-to-line voltage.
 
Article 100
Voltage (of a circuit). The greatest root-mean-square (rms) (effective) difference of potential between any two conductors of the circuit concerned.
 
manuel bonilla said:
What would be the answer to this. In my opinion column 4 would prevail.

It's not a matter of prevailing or not. It is your option. Either one would work. So if you have 4 inches of concrete then you don't need to go down 18".
 