A few questions on this subject. 15A minimum for 1 circuit, 30A for two 2-wire circuits, etc. I believe a multiwire branch circuit qualifies for the 15A minimum, right?
1. Why would anyone use the two 2-wire circuits which would need a 30A disconnect and ground rod, rather than just a 15 or 20A multiwire circuit.
2. Is the 30A thing assuming they are on one phase? If the two circuits are on different phases you'd never need 30A.
(I guess I'm missing the point of the 30A minimum for 2 circuits.)
3. In general, what is the rating of the disconnect when more than one (up to 6) breakers used with no main? Is it sum of the breakers on a phase, rating of the panel, or something else? A 60A main lug panel with two 15A breakers installed. Is that a 60A disconnect? Code reference for this one please.
1. Why would anyone use the two 2-wire circuits which would need a 30A disconnect and ground rod, rather than just a 15 or 20A multiwire circuit.
2. Is the 30A thing assuming they are on one phase? If the two circuits are on different phases you'd never need 30A.
(I guess I'm missing the point of the 30A minimum for 2 circuits.)
3. In general, what is the rating of the disconnect when more than one (up to 6) breakers used with no main? Is it sum of the breakers on a phase, rating of the panel, or something else? A 60A main lug panel with two 15A breakers installed. Is that a 60A disconnect? Code reference for this one please.