Minimum headroom

Status
Not open for further replies.

Grouch1980

Senior Member
Location
New York, NY
Hey guys,
I'm looking at NEC section 110.26(A)(3) in the 2017 version, which is the height of working spaces, and it's stated as 6-1/2 feet. What if you have electrical conduits below this headroom, say at 6' AFF, in front of the panels? They are not blocking the panels. I'm assuming that's still a violation since the conduits are below 6-1/2 feet?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sorry for the bad news but don't believe everything that you read in an article. The 1990 NEC required 6¼' of headroom {110-16(F)}. The 1993 expanded that to the current required 6½' of headroom {110.-16(F)}.
 

Grouch1980

Senior Member
Location
New York, NY
Sorry for the bad news but don't believe everything that you read in an article. The 1990 NEC required 6¼' of headroom {110-16(F)}. The 1993 expanded that to the current required 6½' of headroom {110.-16(F)}.
But but but... it's the internet!! :)

Thanks for the heads up.
 