Minimum height for receptacles

Status
Not open for further replies.
I agree with the other responders. But I will add that the NEC does sometimes give a maximum height.
 
Ada

Ada

Maybe there is a height with the ADA.

. . . Electrical and communications system receptacles on walls shall be mounted no less than 15 in (380 mm) above the floor.
EXCEPTION: These requirements do not appy where the use of special equpment dictates otherwise or where electrical and communications systems receptacles are not intended for use by the building occupants.
ADA / 28 CFR Part 36 4.27.3 1991. Time for a new one!

I think our area does not like a single receptacle to be used for 210.52 spacing, so I would expect that 15" to center is ok for ADA, but entire duplex 15" aff. local.
 
ADA / 28 CFR Part 36 4.27.3 1991. Time for a new one!

I think our area does not like a single receptacle to be used for 210.52 spacing, so I would expect that 15" to center is ok for ADA, but entire duplex 15" aff. local.

For side approach it is 9"

fig6b.gif


Figure 6(b)
High and Low - Side Reach Limits


The 30 by 48 inch wheelchair clear floor space is located a maximum 10 inches (255 mm) from the wall.

Roger
 
For side approach it is 9"

fig6b.gif


Figure 6(b)
High and Low - Side Reach Limits


The 30 by 48 inch wheelchair clear floor space is located a maximum 10 inches (255 mm) from the wall.

Roger

Yeah, I saw that too, but I didn't find any associated text then, now I see it is 4.2.6 (1991). Will that trump 4.27.3? I don't use this book that often.

Though with the image link I assume it is available online now . . .
 
It would for 210.52 recep's.
(4) Located not more than 1.7 m (5 1/2 ft) above the floor.

That would be MAX height, minimum is what was questioned. :smile:

My response was actually to the question of if it was a commercial installation.
 
If it's a commercial then ADA would apply and it is minimum 15" to the center AFF, so it can be higher. Even here where we follow the CA Electrical Code, which is the NEC with ADA amendments they took that out of the book and it is now in the IBC.

So to truly answer your question there is nothing in the NEC about minimum height.
 
Last edited:
If it's a commercial then ADA would apply and it is minimum 15" to the center AFF,

The diagram above is from the ADA guidelines and there is no mention of side approach not being allowed in commercial settings. As a matter of fact, I have installed items at heights per the above diagram in USPS installations.

Roger
 
Appendix A to Part 1191 - Americans with Disabilities Act (ADA) Accessibility Guidelines for Buildings and Facilities

4.27.2 Clear Floor Space. Clear floor space
complying with 4.2.4 that allows a forward or a
parallel approach by a person using a wheelchair
shall be provided at controls, dispensers,
receptacles, and other operable equipment.

4.2.5* Forward Reach. If the clear floor space
only allows forward approach to an object, the
maximum high forward reach allowed shall be 48
in (1220 mm) (see Fig. 5(a)). The minimum low
forward reach is 15 in (380 mm). If the high
forward reach is over an obstruction, reach and
clearances shall be as shown in Fig. 5(b).

4.2.6* Side Reach. If the clear floor space allows
parallel approach by a person in a wheelchair, the
maximum high side reach allowed shall be 54 in
(1370 mm) and the low side reach shall be no less
than 9 in (230 mm) above the floor (Fig. 6(a) and
(b)). If the side reach is over an obstruction, the
reach and clearances shall be as shown in Fig
6(c).
 