Appendix A to Part 1191 - Americans with Disabilities Act (ADA) Accessibility Guidelines for Buildings and Facilities
4.27.2 Clear Floor Space. Clear floor space
complying with 4.2.4 that allows a forward or a
parallel approach by a person using a wheelchair
shall be provided at controls, dispensers,
receptacles, and other operable equipment.
4.2.5* Forward Reach. If the clear floor space
only allows forward approach to an object, the
maximum high forward reach allowed shall be 48
in (1220 mm) (see Fig. 5(a)). The minimum low
forward reach is 15 in (380 mm). If the high
forward reach is over an obstruction, reach and
clearances shall be as shown in Fig. 5(b).
4.2.6* Side Reach. If the clear floor space allows
parallel approach by a person in a wheelchair, the
maximum high side reach allowed shall be 54 in
(1370 mm) and the low side reach shall be no less
than 9 in (230 mm) above the floor (Fig. 6(a) and
(b)). If the side reach is over an obstruction, the
reach and clearances shall be as shown in Fig
6(c).