ptonsparky said:AB states which overloads to use for the protection of motors on the load side of a drive. They had two types listed in the FAQ page I read this morning. One was a melting alloy type with a W heater for class 20 protection, the other was an IEC style, if I remember correctly. Electronic overloads were not to be used.
In order to Comply with the NEC. AB will be happy to comply with it weather it actually provides the intended protection or not.
What I am saying that the only protection meaningful is the electronic overload protection WITHIN the drive for a single motor. When you have multiple motors on a single drive the only effective thermal protection is a winfing embedded thermistor with protective relay connected to it. It is actually an IEC requirement for hazardous area motors, even with a single motor/drive combination.