Minimum Liquidtight length

Status
Not open for further replies.

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Hello all. Is there a minimum that liquidtight can be ran ? I need a nipple into VFD and was checking if there is a code minimum length it can be. Thanks in advance.
No NEC minimum requirement that I am aware of. Probably only customer specs if applicable.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I've only ever heard of a maximum, which I recall is 72 inches (6 feet/1.8 meters).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The is no maximum length in the NEC. NYC has a 6' maximum as a code amendment. I agree that there is no minimum length although if it's used for flexibility then there is probably a minimum length required for that.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
If the fittings can be correctly installed, that should be the minimum length required.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I had a application for short lengths of liquid tight between cabinets, I found T&B made a LT chase connector which worked well
 